Not as far as I'm aware, and there are no relevant measures in BCL that I could find.
To change the curve you can just set the relevant values in the
OS:Curve:Biquadraticobject by clicking on the boiler in your plant loop and scrolling down to the curve parameters (see image). The default is a flat curve withCoefficient1 Constantset to 1 and everything else set to 0. If you changeCoefficient1 Constantto 0.9667 andCoefficient2 xto -0.1667 then that is the same as the condensing boiler in the HospitalLowEnergy.idf example file.See the other answer.
OS:Curve:Biquadraticobject by clicking on the boiler in your plant loop and scrolling down to the curve parameters (see image). The default is a flat curve withCoefficient1 Constantset to 1 and everything else set to 0. If you changeCoefficient1 Constantto 0.9667 andCoefficient2 xto -0.1667 then that is the same as the condensing boiler in the HospitalLowEnergy.idf example file.See the other answer.I think we need more information to solve that part. What values did you use?