If you have to model opening/closing only external doors and windows, there is a simple solution:
(A) You may specify
ZoneInfiltration:EffectiveLeakageArea(s) for every zone, and define a schedule for the flow fraction (0=closed, 1=fully open);For more specialized requirements, the schedule values may be driven by an EMS program (by defining actuators on these schedules)
If you want to model air exchange through external and internal doors/windows, this can be done by setting up an AirflowNetwork for your zones:
(B) for each window/door specify a corresponding
AirflowNetwork:MultiZone:Surfaceand define Leakage Components:set
Window/Door Opening Factor >0(<=1 );set
Ventilation Control Mode=constantnow define a
VentingAvailability Schedule: this will dynamically drive the Venting Window/Door Opening Factor by this formula: [AFN Surface Venting Window/Door Opening Factor] = [Window/Door Opening Factor] * [VentingAvailability](0=closed, 1= fully open). You can verify whether the air flows behave as intended e.g. by checking the output variables:
Key Value =
AirflowNetwork:MultiZone:Surface NameVariable Name =
AFN Linkage Node 1 to Node 2 Mass Flow Rate(from AirflowNetwork:MultiZone:Surface to the other side)
Variable Name =
AFN Linkage Node 2 to Node 1 Mass Flow Rate
(from the other side to AirflowNetwork:MultiZone:Surface )(C) If window/door openings should depend on special user defined conditions, define an EMS Actuator, e.g. myOpenFactor, for one surface of each Door/Window, with
Actuated Component Type =
AirFlow Network Window/Door OpeningActuated Component Control Type =
Venting Opening FactorThe dynamic value of myOpenFactor then is determined by an EMS program. More details can be studied in the Example file
EMSAirflowNetworkOpeningControlByHumidity.idf