1

Can i run OpenStudio-Sketchup model with only assigning thermal zone to the building?what else do i need to provide.?

I have assigned the entire model on 1 thermal zone so that i can run my model in order to generate the window to wall ratio . However the simulation is showing error messages and is always showing "failed" at 75 %.

adhiraj03's avatar
61
adhiraj03
asked 2016-10-29 00:18:49 -0500
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2017-09-03 10:03:14 -0500
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

2

At a minimum the thermal zone should have one or more spaces, those spaced should have surfaces, and the surfaces need constructions. Lastly you need an epw file.

For specific information on why your simulation is failing look at OpenStudio troubleshooting documentation.

David Goldwasser's avatar
20.4k
David Goldwasser
answered 2016-10-31 08:33:11 -0500, updated 2016-10-31 14:37:23 -0500
edit flag offensive 0 remove flag delete link

Comments

And a thermostat...

ljbrackney's avatar ljbrackney (2016-10-31 13:46:14 -0500) edit

@ljbrackney you can run without a thermostat if you don't have an HVAC system. This is done sometimes for passive design studies. HVAC systems and internal loads are optional, but surfaces and constructions are required. Generally a weather file is also required except in special cases.

David Goldwasser's avatar David Goldwasser (2016-10-31 14:36:33 -0500) edit
add a comment see more comments