EnergyPlus HVACCurveFitTool for chiller EIRfPLR curve?

EnergyPlus' Chiller:Electric:EIR requires a quadratic performance curve for it's Electric Input to Cooling Output Ratio Function of Part Load Ratio (EIRfPLR) curve.

Is it possible to create this quadratic curve using EnergyPlus' HVAC Curve Fit Tool?

I can create the biquadratic curves for CAPfT and EIRfT using the tool, but I'm not quite sure how to create the quadratic EIRfPLR curve.

Lyle K's avatar
2.2k
Lyle K
asked 2016-10-14 12:22:44 -0500, updated 2016-10-14 14:59:53 -0500
edit flag offensive 0 remove flag close merge delete

Comments

Does the Chiller:Electric:EIR accept a biquadratic? If not, then the EIRfPLR curve will just represent EIR as a function of part load ratio regardless of lift (dT)?

pflaumingo's avatar pflaumingo (2016-10-14 12:42:13 -0500) edit

Hey @pflaumingo , you're correct, I have edited my question accordingly. I was having flashbacks to my previous eQUEST/DOE-2 days where the chiller EIRfPLR curve would accept a 'biquadratic in ratio & dT' curve to model EIR as a function of both PLR and lift (dT).... old habits die hard, haha.

Lyle K's avatar Lyle K (2016-10-14 15:09:59 -0500) edit
add a comment see more comments

1 Answer

5

From the INPUTS sheet...

DX Coil Type = Other
Independent Variable = Flow or Temperature (either will work)
Curve Type = Quadratic

For the independent variable, either option will work as long as the corresponding column in the performance data is PLR.


The performance data header names are less important than getting the dependent and independent variable data in the correct columns.

MatthewSteen's avatar
10.1k
MatthewSteen
answered 2016-10-14 12:46:22 -0500, updated 2016-10-14 15:46:39 -0500
edit flag offensive 0 remove flag delete link

Comments

Hello,

I am trying to generate EIRfPLR quadratic curve using EnergyPlus' HVAC Curve Fit Tool. The output sheet gives two set of coefficients CAPFTemp and EIRFTemp even though I imputed PLR (Independent variable), Cap and Power (Dependent variable) in the column whereas I expected only one, EIRfPLR. Any insight?

thanks,

Javed's avatar Javed (2019-11-18 11:26:28 -0500) edit

@Javed see the last sentence of my answer. The spreadsheet names the curve objects based on the independent variable selection, so either flow or temp. As long as your data is in the correct column the object names don't matter, just change them before exporting to IDF.

MatthewSteen's avatar MatthewSteen (2019-11-18 12:03:57 -0500) edit

thank you. It helps!

Javed's avatar Javed (2019-11-18 12:27:12 -0500) edit
add a comment see more comments