VRF condenser type report

It seems the condenser type of VRF system in E+ Component Sizing Report is evaporative even we setup as air cooled in idf file.

Please someone check and confirm about this problem.

ngkhanh's avatar
2.2k
ngkhanh
asked 2016-01-27 12:38:16 -0600
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2016-02-01 01:35:38 -0600
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

1 Answer

3

I ran the VariableRefrigerantFlow_5Zone example file and also changed the condenser type to EvaporativelyCooled. The results shown in the Component Sizing Summary using V8.4 appear correct.

The first table denotes the air-cooled simulation while the second table reflects the results of the evap-cooled simulation. The results show the values for autosized input fields.

Top one is air cooled, bottom is evaporatively cooled

rraustad's avatar
13.8k
rraustad
answered 2016-01-27 18:36:17 -0600
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2016-02-01 01:35:09 -0600
edit flag offensive 0 remove flag delete link

Comments

2 tables for difference selection ? i can only get 1 table not both

ngkhanh's avatar ngkhanh (2016-01-28 08:27:33 -0600) edit

I pasted the tables from 2 simulations into a single picture so you could see them both at once. The top table is air-cooled, the bottom table is evaporatively-cooled.

rraustad's avatar rraustad (2016-01-28 08:47:02 -0600) edit