I have another question about EnergyPlus. I made a study with a stair stepped roof, the lower steps seemed to be shaded. Then I deleted all the wall surfaces leaving only roof surfaces and the lower steps were no longer shaded. Can roof surfaces shade other roof surfaces in EnergyPlus?

-Hodor

hodor's avatar
463
hodor
asked 2014-11-19 09:21:17 -0600
__AmirRoth__'s avatar
4.4k
__AmirRoth__
updated 2015-07-10 09:03:47 -0600
edit flag offensive 0 remove flag close merge delete

Comments

add a comment see more comments

2 Answers

7

EnergyPlus surfaces only cast shadows in the direction of their outward facing normal. Roofs face up, so they do now shade anything below them. Shading surfaces are mirrored by default so they cast shadows in all directions. When the building surfaces form an enclosure, all of the expected shading should occur since there will be either vertical walls or downward facing overhangs or soffits to shade surfaces below.

MJWitte's avatar
9.7k
MJWitte
answered 2014-11-21 15:32:39 -0600
edit flag offensive 0 remove flag delete link

Comments

Thanks for those details, I had it backwards.

David Goldwasser's avatar David Goldwasser (2014-11-21 17:48:24 -0600) edit
add a comment see more comments
1

I'm not sure if heat transfer surfaces in EnergyPlus block the sun from both sides by default. Just to confirm it is not an issue you might want to make sure the surface normal isn't reversed on the roof. Also, even if your roofs are correct, when the sun is behind the high end of the roof but at a low angle it would sneak in under the higher roof to hit the lower roof.

David Goldwasser's avatar
20.4k
David Goldwasser
answered 2014-11-21 15:10:25 -0600, updated 2014-11-21 15:22:26 -0600
edit flag offensive 0 remove flag delete link