My questions stems off my recent question regarding district heating/cooling (https://unmethours.com/question/12845...).

So I have this central plant that provides hot water and is used for some elements through the building such as radiant panels. The hot water is also sent to a heat exchanger that has a 40% glycol loop for the heating coils of the buildings AHUs. I am wondering how I would go about modelling this and if there is a way in OpenStudio to say that one side of the heat exchanger has water going through it and the other has glycol fluid going through it. I am assuming it will have to be two plant loops that are connected via this heat exchanger. Any help is appreciated.

Dustin's avatar
1.1k
Dustin
asked 2015-11-20 06:58:19 -0500
Julien Marrec's avatar
29.7k
Julien Marrec
updated 2017-01-27 14:47:29 -0500
edit flag offensive 0 remove flag reopen merge delete

Closed for the following reason "the question is answered, right answer was accepted" by Dustin 2016-02-18 06:52:17 -0500

Comments

add a comment see more comments

1 Answer

7

In EnergyPlus, you can define a FluidProperties:GlycolConcentration object and reference it as the working fluid of a plant loop. Currently this isn't exposed in OpenStudio, so you'd have to use an EnergyPlus measure to set the properties of your glycol loop, after you set them up in the model.

I put one together a while back to let you define arguments for the fluid loop and the glycol concentration:

loop_name = OpenStudio::Ruleset::OSArgument.makeStringArgument("loop_name", true)
loop_name.setDisplayName("Loop Name, e.g. 'GlycolLoop - Heating'")
loop_name.setDescription("Enter the loop to change the working fluid.")
args << loop_name

concentration = OpenStudio::Ruleset::OSArgument.makeDoubleArgument("concentration", true)
concentration.setDisplayName("Concentration of Propylene Glycol solution.")
concentration.setDefaultValue(0.4)
args << concentration

Then in the run section, get the arguments:

#assign the user inputs to variables
loop_name = runner.getStringArgumentValue("loop_name",user_arguments)
concentration = runner.getDoubleArgumentValue("concentration", user_arguments)

Get the loop:

#get list of workspace objects named loop_name
loop = workspace.getObjectsByName(loop_name, true)

Create the idf string and pass it into the workspace:

conc_string = "
FluidProperties:GlycolConcentration,
    ProGly#{concentration}Percent,
    PropyleneGlycol,
    ,
    #{concentration};
    "
idfObject = OpenStudio::IdfObject::load(conc_string)
object = idfObject.get
wsObject = workspace.addObject(object)
new_conc = wsObject.get

And set your loop to reference the fluid property:

if not loop.empty?
    loop[0].setString(1,"UserDefinedFluidType")
    loop[0].setString(2,"ProGly#{concentration}Percent")
end

EDIT: Fluid properties are now exposed in the Plant Loop settings in OpenStudio (as of at least v2.3.0)

ericringold's avatar
10.6k
ericringold
answered 2015-11-20 11:31:01 -0500, updated 2018-05-18 13:59:46 -0500
edit flag offensive 0 remove flag delete link

Comments

Ok so thanks for the answer. I am pretty inexperienced when it comes to coding. I understand that I could probably just copy and run this but I have another questions. In my "Glycol Loop" should I change the fluid type to UserDefineFluidType and then run the EnergyPlus measure? Another question is when should I run the E+ measure, right before I go to run a simulation or while I am still modelling?

Dustin's avatar Dustin (2015-11-30 08:14:58 -0500) edit

could someone please turn this into a measure for people that don't know how to do this? I need ethylene glycol 20% in a model. Trace does this easily.

kramerica's avatar kramerica (2016-04-28 09:57:55 -0500) edit
2

Sure. No guarantees though. https://www.dropbox.com/s/akrdc0hw795...

Extract that into your 'My Measures' folder and you can drag it into the EnergyPlus Measures section in your measure tab.

ericringold's avatar ericringold (2016-04-28 10:23:02 -0500) edit

Thanks @Eric Ringold! I'll test it out and let you know how it works.

kramerica's avatar kramerica (2016-04-28 11:01:04 -0500) edit
add a comment see more comments